Wyze thermostat installation to a 7 wire setup

I cant figure out the set up. I keep getting a wire error. Someone help please. There are two jumping wires and 7 others detailed below

White-e/w
Blue-c
Red-R
Brown-l
Green-G
Yellow-Y
Orange-O

I’m not familiar with this thermostat, do you have a clear reading of what the terminals say?

1 Like

From how it is glued to the board it covers the terminal names. I identified the terminals which the wires are connected to.

What’s the black wire with the resistor jumper to C?

That is to terminal L

Not sure what that would be used for. In older systems it would light up an led in case of a fault, but there’s not implementation for it on newer thermostats. You can probably leave the black wire disconnected then.

The only wires you should have hooked up on the wyze are
Rc: Red
Y1: Yellow
O/B: Orange
C: Blue
G: Green
W1: White

And if you want emergency heat, * jumped to W
Tell wyze you have those wires when setting it up and leave the black wire disconnected.

3 Likes

I hooked those wires and bypassed the error message which seem to have worked.

Thank you!