I’m trying to sort out my Thermostat wiring issues. My furnace/air conditioning unit is up in my attic and hard to get to. But I did and I found that the control board only has three wires that come off of it to the thermostat. Wires are: Red Green and white. Power appears to come from a transformer that is mounted on a ceiling joist. I don’t know why, but they connected the ps to the yellow wire that goes down to the T-stat. So, at the t-stat I have yellow going to the C terminal, Red wire to the Rc terminal, White to W1 and Green to G terminal. The Small blue wire is not connected to anything.
Yeah, somethings not right. The yellow Y at your thermostat shouldn’t be going to C but to Y on the control board. Y is for AC which might explain why AC is not working. Did you install the C wire adapter? Can you post more pictures of the wired wyze thermostat and if possible the control board too?
Here’s how you should have hooked up your C wire adapter.
I’m betting you hooked up the A/C compressor wires to the wrong side of the adapter or interrupted the C wiring to the compressor when you installed the adapter.
Well,
I thought it was working. The ac is not coming on. I’ll have to get back up there and see what I did wrong. It’s not coming on with either of my two units. Heat works fine but the ac is not.
I’ll take and post pictures of my connections.
Thanks
Hi well I have more info.
There are two pig tails that enter the unit. The first pigtail has red, green, yellow and white. This is what you see wired into the adapter.
The second pigtail has, red yellow and white.
Following your diagram I connected the yellow wire to the C wire from the adapter, the red I connected to the to the y wire coming from the adapter.
In this configuration my t-stat has no power and the unit will not turn on at all.
If I connect the red wire to the C wire on the adapter wire and the yellow wire to the y-wire coming from the adapter, my unit starts and I have heat, but no a/c.
From the second pigtail that has the red and yellow wire, there is a white wire connected to a blue wire coming from the circut board cluster of wires. I have no idea what that is used for.
Plus I’m color blind, and have to get my wife to tell me which wire is which.
Thanks for your assistance with this, I’m not afraid to do the work myself, but I’m at a loss on how to make this thing work.
If you look at the picture at the beginning of this post you can see that the small yellow wire and a small red wire are twisted together in the same wire nut.
Just so I’m clear on this, the c wire from the adapter ribbon cable should go to the purple wire and white small wire nut.
That would leave the ribbon Y wire not attached to anything?
I will try your recommendation this morning and report back when done.
You have 2 yellow wires. One goes to your thermostat, that one used to be attached to the red wire, and is now attached to the wyze adapter’s screw terminal that is labeled Y. The other one shouldn’t have been attached to anything.
I’m not asking you to do anything with the Y ribbon wire, leave it wire nutted to the red wire that goes to the A/C unit.
Your C wire will have 3 wires in its wire nut - large purple from furnace, small white to A/C, and the C ribbon cable from your wyze adapter. This is normal.