You would need both of the C adapter wires to be connected to the wyze, or have the common come from the transformer on your aquastat. Unfortunately, there is no way for the current to make a loop through the load if both transformer wires are not connected to it,
Related topics
Topic | Replies | Views | Activity | |
---|---|---|---|---|
Wyze thermostat HELP! | 14 | 768 | October 6, 2021 | |
Wyze thermostat wiring assistance | 5 | 862 | January 8, 2021 | |
Wyze Thermostat 24 volt power adapter question | 4 | 1193 | January 11, 2021 | |
Thermostat Power supply | 6 | 1465 | January 31, 2021 | |
Old Gas Furnace with Wall Adapter for C Wire | 9 | 1153 | June 13, 2021 |