Hello… pls help. I can’t install my Wyze thermostat because I only have red white and green wires on my old Honeywell thermostat. I live in Canada so don’t have AC… attached is a picture
Do you have a picture of the heating device?( furnace/ boiler)
Thanks Speadie… was reading some of your old posts but just want to make sure… here’s the photo of my furnace…
You have the furnace board control the heating fan, and not the thermostat.
Then you would have a spare green wire that can be connected to C instead of G on both ends.
You would lose the ability to control the fan manually or through the thermostat though.
Otherwise you would need to run a new wire.
Ok, right now the fan is automatically activated by the thermostat depending on the temperature setting… I guess the safest is run a separate wire
Thanks Speadie, one more thing… where do I put the C wire on the Furnace’s board?
This topic was automatically closed 90 days after the last reply. New replies are no longer allowed.