Thermostat, No C terminal on "control board"

Hello! I have a pretty old combo heat and AC unit on my roof. I didn’t have a c wire so I went up to find the control panel and I’m only seeing 4 terminals r, y, g and w.

Anyone have an idea where or what I should do to get the c wire adapter connected correctly?

Thank you!

Here are some pictures:

Maybe something like this would work if I plug it in in the attic and run the wire down with the existing thermostat wires?

Your 2nd picture shows the 24v transformer, trace the wire from R terminal back to the transformer. The other wire on the transformer will be the C wire, trace that wire out to see where it connects. Worse case you can cut that C wire, strip it back a bit and use a wire nut to connect it back together with the C wire adapter. If you go this route, make sure you turn off breaker just to be safe.

Is there another screw terminal right here?
image
Is that blue wire available at your thermostat?

If so, connect the blue wire to this terminal and to your C terminal on the wyze.
Your thermostat wiring needs to be re-sleeved or insulated with electrical tape, the insulation is pretty compromised.

Thank you so much! I went back up the roof today and was able to get it all working with your advice!

Excellent!