The Y wire from the thermostat should connect to the Y terminal on the furnace. The Y1 wire from the outside unit should also connect to that same Y terminal on the furnace.
The red and white wire that go to the outside unit control that unit’s contactor. You seem to have created a loop by taking out the Y terminal on the furnace
The wires around the transformer aren’t clear enough to tell where they are going, Where exactly do the wire labeled W, R, and C go? Also, where does that white wire with black stripes go?
I don’t see an issue with the Y connector, necessarily. If the wires do what I think they do, that part would be fine.
The C wire appears to be grounded to the gas valve instead of going into the expected wire nut- if the white wire with black stripes is the wire I think it is, then that would be your C.
I just need verification that the W wire is going back to the control for the gas valve, and the C and R are both attached to different sides of the 24v transformer coil to be certain.
The C wire appears to be grounded to the gas valve instead of going into the expected wire nut- if the white wire with black stripes is the wire I think it is, then that would be your C.
That was it. My common should have been connected to these wires. it is working now. Thank you all for the help. My wife says thanks